Forum > Heating & Air Conditioning Repair

Newbie needs help wiring Trane TCONT802AS32DAA

<< < (3/3)

handsmcgee:
I am familiar with that Tstat. it does appear to be wired properly. The only question is the W1/O terminal on the left and W1 on the right. Of those terminals one will run 1heat 1cool which is what you want and the other is for staging heat pump. You will need to go to the setup process to make that stat know what sytem to operate. To get to the setup function press the system button once then at the bottom press the 2nd and 4th key hold and hold til screen changes. for a gas furnace w/ a/c your setup will follow;function then setting,  0120=20, 
0130=12
0140= month digit
0150= day digit
0170=1
0180=0
0220=3
0240=5
0280=0
0300=0
0320=0
0330=2
0340=0
and if you want to use the a/c as a dehumidifier.
0380=1 otherwise use 0 to turn this function off
0500=0
0510=0
0520=0
0530=0
0580=5
0600=85
0610=55
0640=12
0650=90
0660=90
0670=0
0680=2
0690=2
0700=0
0710=0
press done to exit and the t-stat should be programmed for 1heat 1cool or gas w/ air conditioning. hope this helps

handsmcgee:
Just noticed you may have the wrong honeywell manual you may want to look up the manual for th TH8320 honeywell Thermostat. This might clear the water so to speek.

kenora:
THANKS...... Got it done and all is working as advertised  :)

Navigation

[0] Message Index

[*] Previous page

Go to full version