Author Topic: Carrier split system heat pump  (Read 1421 times)

Offline GCLOER

  • VIP Member
  • Member Since: Jan 2012
  • Posts: 1
Carrier split system heat pump
« on: January 06, 2012, 08:34:58 PM »
I have a 3 ton Carrier split system heat pump.  The condenser fan motor bearing locked
down.  I replaced the motor.  The old motor was an OEM 3 wire motor. I replaced with a
universal 4 wire motor.  Installed a 5 mfd cap.  Removed the wires from the duel cap on
the motor. ran my blk wire to the defrost board. ran my yellow wire to the contactor.
brown and brwn/wht wire to the new 5/440 cap.

Started the unit. verified proper rotation. Unit ran for about 10 seconds. contactor disengauged
Defrost board took it out.  no 24 volts present at the contactor.  I checked my low voltage wires
I have 24 volts across yellow and common going to the defrost board.  Board kept the unit off
for about 5 minutes. Then, click the 24 volts was restored to the contactor for about 10 seconds- then off again for 5 minutes.

I disconnected power leads to the compressor .  Restarted  condenser fan motor came on and stayed on.  Reattached compressor wires- restarted  compressor pulled 8 amps.
RLA on compressor is 18 amps.
Checked pressures- compressor is running   I did not see a low pressure switch. didnn't look that close either.

any ideas

Offline jumptrout51

  • Technician
  • Member Since: Nov 2007
  • Posts: 1879
  • Country: us
    • Buy me a beer through paypal
Re: Carrier split system heat pump
« Reply #1 on: January 08, 2012, 07:42:59 AM »
Sounds like a low pressure lockout to me.
Take a Kid fishing.

Offline Icehouse

  • Technician
  • Member Since: Oct 2008
  • Posts: 566
    • hvacbob
Re: Carrier split system heat pump
« Reply #2 on: January 29, 2012, 03:14:25 PM »
 ???  If the RLA is 18 and you only read 8 on start-up makes no sense. Starting Amp's are 5 times the running amps. :)
NATE, NCCER, PHCC,HVAC Certified Instructor
Member RSES, US Army Refrigeration Specialist(Retired), Former Refrigeration Teacher NYC Board of Ed.
a tragedy has happen to me : http://web.me.com/zenzoidman/Bobice/

 

Carrier Heat pump OAT 25HPA

Started by chrissymustang

Replies: 4
Views: 4064
Last post February 02, 2011, 05:21:06 PM
by chrissymustang
Carrier Heat Pump How long should a dual run capacitor last

Started by MerciMe

Replies: 2
Views: 3969
Last post July 21, 2011, 06:56:41 PM
by jumptrout51
Carrier electric heat

Started by jdman

Replies: 20
Views: 6725
Last post October 17, 2008, 10:26:23 PM
by jdman
Heat Pump Defrosting

Started by Icehouse

Replies: 3
Views: 3568
Last post December 27, 2008, 03:57:05 AM
by Icehouse
Heat Pump Electrical Componet Check

Started by Icehouse

Replies: 1
Views: 5558
Last post February 25, 2009, 08:00:45 AM
by thermodix
Maintenance Of Residential Split System Air Conditioners

Started by Icehouse

Replies: 0
Views: 4508
Last post January 24, 2009, 06:45:03 PM
by Icehouse