Author Topic: ICP TempStar NUGK075DG07  (Read 236 times)

Offline Jesster

  • VIP Member
  • Member Since: Dec 2014
  • Posts: 3
ICP TempStar NUGK075DG07
« on: February 17, 2015, 11:02:43 PM »
I have a friend with a ICP NUGK075DG07 furnace.  He needs a new flame sensor and the one we took out of it doesn't match the single tube-single wire sensors on the parts sites.  I have two pictures one which shows the square edges and length and the other picture has the three electrical contacts (only two of which were used).  Is this an OEM flame sensor? It looks adjustable, which is usually not the case for factory parts like this.  The printing says: CAM STAT L59-78-A.  Anyone have any ideas.  The part I found was a 1380679 ICP sensor which supposedly replaced the original 1001358.
« Last Edit: February 17, 2015, 11:04:18 PM by Jesster »

Offline Airczech

  • VIP Member
  • Member Since: Mar 2015
  • Posts: 2
Re: ICP TempStar NUGK075DG07
« Reply #1 on: March 03, 2015, 02:37:29 PM »
Be careful what you r looking for. This is not a flame sensor. Its a main limit switch, adjustable 120-250F with a fixed differential of 30F. They must be replaced with the OEM part. Match the temperature setting of the old part and test it, make sure it operates properly. Limit switch should shut the burner down no later than 3-3.5 minutes after the main burner ignition, when the blower fails.
Cam-Stats are still available, you should be able to get the same part.

 

Tempstar Heat Pump not running but Air handler is

Started by lgmccoy1

Replies: 4
Views: 6833
Last post November 19, 2010, 06:16:05 AM
by jumptrout51
Tempstar heat pump won't initiate defrost cycle

Started by lgmccoy1

Replies: 13
Views: 11227
Last post December 24, 2010, 12:53:31 PM
by jumptrout51
1992 model NPADE29AB03 Tempstar(mfd. by ICP) shutting down

Started by thatsnotwhatyurmothersaid

Replies: 35
Views: 5958
Last post September 11, 2014, 06:58:08 AM
by AJ