H9MPD100J14A2 & L022488510
« on: December 06, 2010, 11:22:06 PM »
Heil product which is located in a basement.  The numbers on the side of the unit are:  H9MPD100J14A2  L022488510

This unit has two 3" PVC pipes running up vertically (for 3 feet), then run horizontally for about 17 feet before joining together into a single pipe.  The single pipe then runs outside.  One pipe is the fresh combustion air; the other is the flue.

At the unit, a substantial amount of condensate drips from both pipes.

What can yall tell me about this unit?
May the hinges of our friendship
        never grow rusty.

About the icons: The beer is tip link, if a tech saves ya some money buy em a 6 pack. The small green square=personal message. The green dot is a link to my web page on appliance repair and other general BS I love to post. The letter sends me email.
I love fan letters! LOL

Offline jumptrout51

  • Technician
  • Member Since: Nov 2007
  • Posts: 1879
  • Country: us
    • Buy me a beer through paypal
Re: H9MPD100J14A2
« Reply #1 on: December 07, 2010, 07:01:09 AM »
Your horizontal run should rise a minimum of 1/4 inch per foot.
The exhaust and fresh air might be connected to the wrong outlet/inlet on the transition.
The outside portion must have a 90 degree down on the exhaust connection.
The draft inducer should be internally drained to a condensate trap.