Re: Goodman Furnace Ignitor Problem
« Reply #10 on: November 14, 2010, 10:56:23 AM »
Thanks very much for the advice. I am passing this on to the guy who is working on this unit. He will be going back out to the customer's house in the morning and I will let you know if he can get this unit going.

Offline iceman

  • Technician
  • Member Since: May 2009
  • Posts: 39
  • Country: us
Re: Goodman Furnace Ignitor Problem
« Reply #11 on: November 20, 2010, 04:15:55 PM »
The unit is now running. He told me the common coming off the transformer had to be connected to the ground on the board. This unit was originally a standing pilot furnace that had been retrofitted. Customer told the technician it hadn't worked right since it was retrofitted by another guy quite sometime ago. After several attempts to get the previous guy back out to repair it, he got tired of waiting so he called my buddy. The unit is running ok now. Thanks for all the help guys!

 

Maytag Airconditioner problem

Started by smckeown

Replies: 8
Views: 8111
Last post July 25, 2007, 05:33:44 PM
by AJ
Airtemp furnace

Started by maypo52

Replies: 9
Views: 10908
Last post March 05, 2008, 02:36:32 PM
by JWWebster
whirpool furnace fs643-125cr

Started by ddh

Replies: 2
Views: 4335
Last post July 04, 2008, 09:44:24 AM
by ddh
Rheem Furnace needs a new Thermo Coupler

Started by rezman6

Replies: 3
Views: 7922
Last post October 31, 2008, 08:07:56 AM
by Icehouse
Furnace fan keeps running after normal shutoff by thermostat.

Started by hleebeard@sbcglo

Replies: 1
Views: 7632
Last post January 10, 2009, 09:00:48 PM
by JWWebster
Annual Furnace Tune Up and Maintenance

Started by Icehouse

Replies: 0
Views: 4487
Last post January 24, 2009, 07:28:17 PM
by Icehouse