Author Topic: york 80 furnace mod. # p4hua12n06401a ser. # wemm01044  (Read 1563 times)

Offline repairguy42

  • Technician
  • Member Since: Jan 2010
  • Posts: 51
york 80 furnace mod. # p4hua12n06401a ser. # wemm01044
« on: February 17, 2013, 08:41:16 PM »
igniter comes on, gas ignites and goes out in 6 seconds.  red light on board comes on and goes out.   then that cycle reapeats. need help. thanks

Offline jumptrout51

  • Technician
  • Member Since: Nov 2007
  • Posts: 1879
  • Country: us
    • Buy me a beer through paypal
Re: york 80 furnace mod. # p4hua12n06401a ser. # wemm01044
« Reply #1 on: February 18, 2013, 07:35:40 AM »
Make sure all burners are lit for the short duration.
Pay special attention to the burner at the flame sensor.
Clean the flame sensor probe.
A dirty sensor probe can cause this issue.
It may not look dirty.
A few swipes with fine sandpaper should do it.
Take a Kid fishing.

 

Airtemp furnace

Started by maypo52

Replies: 9
Views: 10411
Last post March 05, 2008, 02:36:32 PM
by JWWebster
whirpool furnace fs643-125cr

Started by ddh

Replies: 2
Views: 4009
Last post July 04, 2008, 09:44:24 AM
by ddh
Rheem Furnace needs a new Thermo Coupler

Started by rezman6

Replies: 3
Views: 7585
Last post October 31, 2008, 08:07:56 AM
by Icehouse
Furnace fan keeps running after normal shutoff by thermostat.

Started by hleebeard@sbcglo

Replies: 1
Views: 7397
Last post January 10, 2009, 09:00:48 PM
by JWWebster
Annual Furnace Tune Up and Maintenance

Started by Icehouse

Replies: 0
Views: 4307
Last post January 24, 2009, 07:28:17 PM
by Icehouse
How does a Warm Air Heating Furnace work?

Started by Icehouse

Replies: 0
Views: 7489
Last post January 24, 2009, 07:31:22 PM
by Icehouse