Late last minute call out of area to a ncoo GE Profile. It had previously been serviced approx 30 days ago for ncoo. Owner and extended warranty co both told me that the previous servicer said unit had a sealed system leak. I found a access valve installed, ff @ 74 deg and fz @ 79. Variable speed compressor running and cool, no heat in liquid line and a slightly cool suction line. Initial low side pressure @ -4 psi. Looked for signs of leak before and after charging - nothing found. Charged unit so customer could use the unit till a resolution was achieved. The problem comes in with two things. I charged the unit to approx 3psi - No temp changes to anything. Kept going up to 5 then 10 then 15, etc till I finally got some heat in the condenser about 1/3 of the way through at 35psi. Also the compressor had a sort of dull light rod knock sound - lighter when settled and a bit more pronounced when adding refrigerant. The temp started dropping quickly then but I know somethings wrong here. I've never charged a residential unit to that high of a low side pressure before. I find it odd that the unit would have a leak and a bad compressor but I know it's possible. Just not used to charging variable speed units so it leaves me with questions that with a recip comp I would not have. Wish I would have had time to add a high side valve. Opinions please. Thanks